Filter Attributes - Point Attributes
The following filter attributes represents properties from the point configuration record. They are available for use throughout CygNet Software.
- Point: General
- Point: History
- Point: Point Reference
- Point: Application
- Point: Alarm (PNT)
- Point: Alarm (Scheme 0)
- Point: Scaling
- Point: HyperPoint
Point: General
See PNT Editor - General Page for more information.
| Attribute | Attribute Name | Description | User Values |
|---|---|---|---|
|
Active Status |
activestatus |
This attribute is used for filtering on the status of the point. |
0, N (no) or 1, Y (yes) |
|
Allowed Updates |
allowedupdates |
This attribute is used for filtering on the setting of update values for the alarm. |
B (Update All) T (Internal /External) C (Internal User) I (Internal) X (External User) E (External) U (User) N (Updates None) |
|
Allowed Updates Description |
allowedupdates_desc |
This attribute is used for filtering on a description of the Allowed Updates; for example, "Update All" |
Text |
|
Calc Parameter Error Exists |
calcparmerror |
This attribute is used for filtering on the alarm that has a calculation parameter error. A calc parm error is set by the PNT if the point contains invalid calculation parameters. |
0 or 1 |
|
Comment |
comment |
This attribute is used for filtering a comment included in the alarm record. Check spelling; when possible, use the wildcard *. |
Text |
|
Display Attribute |
displayattribute |
This attribute is used for filtering on the display attribute for the alarm condition. |
Text |
|
Display Attribute Desc |
displayattribute_desc |
This attribute is used for filtering on the display attribute description for the alarm |
Text |
|
Facility ID |
facilityid |
This attribute is used for filtering on the Facility ID of the alarm. |
Alphanumeric |
|
Full Tag |
tagfull |
This attribute is used for filtering on the full tag of the alarm; for example, SITE.SERVICE.POINTID:LONGID. |
Alphanumeric |
|
General Point Config Error Exists |
generalconfigerror |
Attribute is used if a general point configuration error exists in the alarm. A general config error is set by the PNT for a variety of reasons, for example:
|
0 or 1 |
|
GNS ID Entry Error Exists |
gnsidentryerror |
This attribute is used for filtering on a GNS ID entry that is in error for the alarm. This option can be useful for troubleshooting. For instance, you can filter to show those alarms that have a problem with a GNS ID. A GNS ID entry error is set by the PNT if a GNS ID is configured on a point which does not exist in the GNS. |
0 or 1 |
|
Initial Type |
initialtype |
This attribute is used for filtering on the initial type for the alarm when it is accessed (for example, (R)estored from the persist file or (I)nitialized.) |
Text |
|
Initial Type Desc |
initialtype_desc |
This attribute is used for filtering on a text description of the initial type. |
None, Restore, Service Configuration, Specified Value |
|
Initial Value |
initialvalue |
This attribute is used for filtering on the initial value for the alarm. |
Alphanumeric |
|
Key Field Entry Error Exists |
keyfieldentryerror |
This attribute is used for filtering on a key field entry error that exists in the point’s alarm condition. A key field entry error is set by the PNT if a referenced point does not exist. Does not apply to the OPCIS. |
0 or 1 |
|
Long Description |
longdescription |
This attribute is used for filtering on the long description of the alarm. |
Text |
|
Long Point ID |
pointidlong |
This attribute is used for filtering on the long point ID of the alarm, i.e., Facility_UDC, for example, METER04_LTANK. |
Alphanumeric |
|
Long Tag |
taglong |
This attribute is used for filtering on the long tag of the point’s alarm condition, which would be SITE.SERVICE:FacilityID_UDC. |
Alphanumeric |
|
Manual Input Enabled |
manualinputenabled |
This attribute is used for filtering on whether or not manual input is enabled for the alarm. |
0 (no) or 1 (yes) |
|
Point Data Type |
pointdatatype |
This attribute is used for filtering on the point data type for the alarm (for example, AI for Analog Input, AO for Analog Output, DO for Digital Output, etc.) |
AI, AO, DI, DO, EI, EO, SI, SO |
|
Point Data Type Desc |
pointdatatype_desc |
This attribute is used for filtering on the description of the point data type for the alarm (for example, Analog Input, Digital Output, etc.) |
Text |
|
Point Has Comment |
hascomment |
This attribute is used for filtering on the alarm that has a comment. |
0 or 1 |
|
Point ID |
pointid |
This attribute is used for filtering on the alarm’s short point ID (for example, 8 characters, such as 00000255). |
Numeric |
|
Point Scheme |
pointscheme |
This attribute is used for filtering on the Point Scheme used for describing point states and alarm conditions. The CygNet Standard Point Scheme is 0. |
0 (or user-customized) |
|
Point Scheme Description |
pointschemedesc |
This attribute is used for filtering on the name of the global Point Scheme for an alarm. The default is CygNet Standard. |
CygNet Standard (or user-customized) |
|
Security Application |
securityapp |
This attribute is used for filtering on the security application for the alarm. |
Text |
|
Service |
service |
This attribute is used for filtering on the service for the alarm, for example, UIS, SVCMON, OPCIS. |
Text |
|
Site |
site |
This attribute is used for filtering on the site for the alarm. |
Text |
|
SiteService |
siteservice |
This attribute is used for filtering on the Site.Service for the alarm. |
Text |
|
Spare |
spare |
This attribute is used for filtering on an attribute internal to the CygNet application. |
Text |
|
System Desc |
system_desc |
This attribute is used for filtering on the System description for an alarm. |
Text |
|
System Name |
systemname |
This attribute is used for filtering on the System name for an alarm. |
Text |
|
Tag |
tag |
This attribute is used for filtering on the tag for the point; for example, Site.Service.PointID. |
Text (alphanumeric) |
|
Uniform Data Code |
uniformdatacode |
This attribute is used for filtering on the uniform data code (UDC) for an alarm. |
Text (alphanumeric) |
|
Uniform Data Code Desc |
uniformdatacode_desc |
This attribute is used for filtering on the point’s UDC description for an alarm. |
Text |
Point: History
See PNT Editor - History Page for more information.
| Attribute | Attribute Name | Description | User Values |
|---|---|---|---|
|
Compression Deviation |
compressiondeviation |
This attribute is used for filtering on the Compression Deviation option. Note: This attribute is an alias which will be used instead of History Deadband. |
Numeric |
|
Compression Type |
compressiontype |
This attribute is used for filtering on the Compression Type option. |
Text |
|
Force Current Value |
forcecurrentval |
This attribute is used for filtering on the Action: Force current value option. Note: This attribute is an alias which will be used instead of Force History. |
Text |
|
Force Evaluation on Update |
forceevaluationonupdate |
This attribute is used for filtering on the Force evaluation on update without changed value option. Note: This attribute is an alias which will be used instead of Force History On Update. |
0 or 1 |
|
Force History |
forcehistory |
Obsolete. This attribute is used for filtering on the Force Logging option. This attribute is shown for backwards compatibility. See Force Current Value for new alias value. |
0 or 1 |
|
Force History On Update |
forcehistoryonupdate |
Obsolete. This attribute is used for filtering on a reporting history option. This attribute is shown for backwards compatibility. See Force Evaluation on Update for new alias value. |
0 or 1 |
|
Force Period |
forceperiod |
Obsolete. This attribute is used for filtering on a history range for the force history update. This attribute is shown for backwards compatibility. See Maximum Reporting Interval for new alias value. |
Numeric |
|
History On Line Days |
historyonlinedays |
Obsolete. This attribute is used for filtering on a VHS point history option. This attribute is shown for backwards compatibility. See Keep Values Within Days for new alias value. |
Numeric |
|
Keep Values Within Days |
keepvaluewithindays |
This attribute is used for filtering on the Keep values within last <n> days option (for example, 30). Note: This attribute is an alias which will be used instead of History On Line Days. |
Numeric |
|
Maximum Reporting Interval |
maximumreportinginterval |
This attribute is used for filtering on the Maximum reporting interval <n> minutes option. Note: This attribute is an alias which will be used instead of Force Period. |
Numeric |
|
Minimum Evaluation Time |
minimumevaluationtime |
This attribute is used for filtering on the Minimum evaluation time <n> seconds option. |
0 or 1 |
|
Report on Next Update |
reportonnext |
This attribute is used for filtering on the Action: Report next value option. |
Text |
|
Report VHS |
reportvhs |
This attribute is used for filtering on the Report values to history option. |
0 or 1 |
Point: Point Reference
See PNT Editor - Point Reference Page for more information.
| Attribute | Attribute Name | Description | User Values |
|---|---|---|---|
|
External ID |
externalid |
This attribute is used for filtering on the External ID for the alarm. |
Numeric |
|
External ID Type |
externalidtype |
This attribute is used for filtering on the External ID type for the alarm. |
Alphanumeric |
|
External ID Type Desc |
externalidtype_desc |
This attribute is used for filtering on the External ID type description for the alarm. |
Text |
|
Point Has External ID |
hasexternalid |
This attribute is used for filtering on an alarm with an External ID property in the point configuration record. |
0 or 1 |
|
Point Reference Type |
pointreferencetype |
This attribute is used for filtering on a table-driven field that describes the function of an alarm’s point tag reference. |
Numeric |
|
Point Reference Type Desc |
pointreferencetype_desc |
This attribute is used for filtering on the description of the point reference type for an alarm. |
Text |
|
Reference Long Point ID |
referencepointidlong |
This attribute is used for filtering on the long point ID for the alarm that is application specific and is used by scripts and SVCMON and OPCIS. |
Alphanumeric |
|
Reference Point ID |
referencepointid |
This attribute is used for filtering on the reference point ID for the point that is application specific (used by scripts and SVCMON and OPCIS). |
Numeric |
|
Reference Service |
referenceservice |
This attribute is used for filtering on the reference service for the alarm that is application specific (used by scripts, SVCMON and OPCIS.) |
Text |
|
Reference Site |
referencesite |
This attribute is used for filtering on the reference site for the alarm that is application specific (used by scripts, SVCMON and OPCIS). |
Text |
Point: Application
See PNT Editor - Application Page for more information.
| Attribute | Attribute Name | Description | User Values |
|---|---|---|---|
|
Any User Flag Set |
anyuserflag |
This attribute is used for filtering on an alarm that has an internal user flag set. |
0 or 1 |
|
Any Verified Flag Set |
anyverifiedflag |
This attribute is used for filtering on an alarm that has an internal verified flag set. |
0 or 1 |
|
General 1-3 |
general1 general2 general3 |
These data fields are used for filtering on a user-defined attribute from the alarm’s application record. |
Text |
|
Indexed 1-3 |
indexed1 indexed2 indexed3 |
These indexed fields are used for filtering on the user-defined attribute from the PNT record for the alarm. |
Text |
|
Last Questionable Change Timestamp |
questtimestamp |
This attribute is used for filtering on the last timestamp indicating when there was a questionable change for the alarm. See Timestamps in the Data section for more information. |
Numeric |
|
Last Verified Change Timestamp |
verifiedtimestamp |
This attribute is used for filtering on the last verified timestamp change for the alarm. See Timestamps in the Data section for more information. |
Numeric |
|
Questionable Flag |
questionableflag |
This attribute is used for filtering on a user-defined flag in the alarm. |
0 or 1 |
|
Table Driven 1 Table Driven 2 Table Driven 3 |
tabledriven1 tabledriven2 tabledriven3 |
These fields are used for filtering on a user-defined attribute from the PNT record for an alarm. |
Text |
|
Table Driven 1 Desc Table Driven 2 Desc Table Driven 3 Desc |
tabledriven1_desc tabledriven2_desc tabledriven3_desc |
These fields are used for filtering on user-defined attribute description from the PNT record for an alarm. |
Text |
|
User Flag 1-8 |
userflag1 - userflag8 |
This attribute is used for filtering on a general user-defined attribute from the PNT record for the alarm. |
0 or 1 |
|
Verified Flag 1-4 |
verifiedflag1 verifiedflag2 verifiedflag3 verifiedflag4 |
This attribute is used for filtering on a user-defined attribute from the PNT record for the alarm. |
0 or 1 |
Point: Alarm (PNT)
See the appropriate PNT Editor page (Analog, Digital, Enumeration, String) for more information.
| Attribute | Attribute Name | Description | User Values |
|---|---|---|---|
|
Alarm Category |
alarmcategory |
This attribute is used for filtering on the alarm category of the point’s alarm (PNT only). |
Alphanumeric |
|
Alarm Category Description |
alarmcategory_desc |
This attribute is used for filtering on the description of the alarm category that matches the alarm category table entry. Make sure that the spelling, including capitalization, is correct (PNT only). |
Text |
|
Alarm Deadband |
alarmdeadband |
This attribute is used for filtering on a point having an alarm deadband entry (for example, 5, 10, etc.). (PNT). |
Numeric |
|
Configurable Bit 01-15 Alarm Priority |
alarm01priority - alarm15priority |
This attribute is used for filtering on an alarm’s numeric alarm priority (PNT). |
0-99 |
|
Configurable Bit 01-15 Calc Parm 1 |
cfgbit01calcparm1 - cfgbit15calcparm1 |
This attribute is used for filtering on a Calculation Parameter 1 for the alarm condition (PNT). |
0 or 1 |
|
Configurable Bit 01-15 Calc Parm 2 |
cfgbit01calcparm2 - cfgbit15calcparm2 |
This attribute is used for filtering on the Calculation Parameter 2 for the alarm condition (PNT). |
0 or 1 |
|
Configurable Bit 01-15 Enabled |
cfgbit01enabled - cfgbit15enabled |
This attribute is used for filtering on an alarm with a specific alarm bit enabled (PNT). |
0 or 1 |
|
Configurable Bit 01-15 GNS ID |
cfgbit01gnsid - cfgbit15gnsid |
This attribute is used for filtering on an alarm with a GNS ID (PNT). |
Alphanumeric |
|
Configurable Bit 01-15 Report CAS |
cfgbit01reportcas - cfgbit15reportcas |
This attribute is used for filtering on an alarm, which has a bit set to report to the CAS (PNT). |
0 or 1 |
|
Configurable Bit 01-15 Report GNS |
cfgbit01reportgns - cfgbit15reportgns |
This attribute is used for filtering on an alarm, which has a configurable bit set to report to the GNS (PNT). |
0 or 1 |
|
Configurable Bit 01-15 Reporting Delay |
cfgbit01rptdelay - cfgbit15rptdelay |
This attribute is used for filtering on the alarm, which has a Reporting Delay bit set (PNT). |
0 or 1 |
|
Digital Off String |
digitaloffstring |
This attribute is used for filtering on a Digital OFF string set to Off for the alarm (PNT). |
0 or 1 |
|
Digital ON String |
digitalonstring |
This attribute is used for filtering when the Digital ON string is set to ON for the alarm (PNT). |
0 or 1 |
|
Does Any Config Bit have a GNS ID |
anycfgbithasgnsid |
This attribute is used for filtering on a configurable bit that has a GNS ID for the alarm (PNT). |
0 or 1 |
|
Does Any Config Bit have Rptg Delay |
anycfgbithasrptdly |
Attribute is for a configurable bit that has a Reporting Delay for the alarm (PNT). |
0 or 1 |
|
Enum Table Name |
enumtablename |
This attribute is used for filtering on the enumeration alarm’s table name (PNT). |
Text |
|
History Deadband |
historydeadband |
This attribute is used for filtering on the History Deadband of the alarm. |
Numeric |
|
Is Any Config Bit Enabled |
anycfgbitenabled |
This attribute is used for filtering on a configurable bit enabled for the alarm (PNT only). |
0 or 1 |
|
Is Any Config Bit Reporting to CAS |
anycfgbitrptgcas |
This attribute is used for filtering on a configurable bit reporting to the CAS (PNT only). |
0 or 1 |
|
Is Any Config Bit Reporting to GNS |
anycfgbitrptggns |
This attribute is used for filtering on a configurable bit that is reporting to the GNS. (PNT only) |
0 or 1 |
|
Maximum Setpoint |
maxsetpoint |
This attribute is used for filtering on the maximum setpoint for the alarm (PNT). |
Numeric |
|
Minimum Setpoint |
minsetpoint |
This attribute is used for filtering on the minimum setpoint for the alarm (PNT). |
Numeric |
|
Report Alarm Delay |
reportalarmdelay |
This attribute is used for filtering on alarm reporting delay to the CAS or to the GNS. |
0 or 1 |
|
Report Delay Value Units |
reportdelayunits |
This attribute is used for filtering on the alarm’s delay value units. |
Text |
|
Report Delay Value Units Description |
reportdelayunits_desc |
This attribute is used for filtering on the description of the alarm’s delay value units. |
Text |
|
Suppress Alarms Enabled |
suppressalarmsenabled |
This attribute is used for filtering on whether an alarm condition is suppressed for the point (PNT). |
0 or 1 |
|
Suppress Alarms End On Date/Time |
suppressalarmsendondatetime |
This attribute is used for filtering on Suppression for the point’s alarm condition that ends on a date and time (PNT). |
0 or 1 |
|
Suppress Alarms End On Normal |
suppressalarmsendonnormal |
This attribute is used for filtering on Suppression for the point’s alarm condition that ends when the normal point state occurs (PNT). |
0 or 1 |
Point: Alarm (Scheme 0)
| Attribute | Attribute Name | Description | User Values |
|---|---|---|---|
|
Alarm Deadband |
alarmdeadband |
This attribute is used for filtering on a point having an alarm deadband entry (for example, 5, 10, etc.). (PNT). |
Numeric |
|
Alarm Priority |
alarmpriority |
This attribute is used for filtering on the priority number for the alarm. |
0-99 |
|
Digital Alarm Enabled |
digitalalarmenabled |
This attribute is used for filtering on whether a digital alarm is enabled. |
0 or 1 |
|
Digital Alarm GNS ID |
digitalalarmgnsid |
This attribute is used for filtering on the GNS ID of a digital alarm. |
Alphanumeric |
|
Digital Alarm When Off |
digitalalarmwhenoff |
This attribute is used for filtering on whether the digital alarm calcparm 1 bit is set. |
0 or 1 |
|
Digital OFF String |
digitaloffstring |
This attribute is used for filtering on a Digital OFF string set to Off for the alarm (PNT). |
Text |
|
Digital ON String |
digitalonstring |
This attribute is used for filtering when the Digital ON string is set to ON for the alarm (PNT). |
Text |
|
Enum Alarm 1 - 6 Enabled |
enumalarm1enabled enumalarm2enabled enumalarm3enabled enumalarm4enabled enumalarm5enabled enumalarm6enabled |
This attribute is used for filtering on whether an enumeration alarm (1 - 6) is enabled. |
0 or 1 |
|
Enum Alarm 1 - 6 GNS ID |
enumalarm1gnsid enumalarm2gnsid enumalarm3gnsid enumalarm4gnsid enumalarm5gnsid enumalarm6gnsid |
This attribute is used for filtering on the GNS ID of an enumeration alarm (1 - 6). |
Alphanumeric |
|
Enum Alarm 1 - 6 Value |
enumalarm1value enumalarm2value enumalarm3value enumalarm4value enumalarm5value enumalarm6value |
This attribute is used for filtering on the value of an enumeration alarm (1 - 6). |
Alphanumeric |
|
Enum Table Name |
enumtablename |
This attribute is used for filtering on the enumeration alarm’s table name (PNT). |
Text |
|
High Alarm Enabled |
highalarmenabled |
This attribute is used for filtering on whether a high alarm bit is enabled. |
0 or 1 |
|
High Alarm GNS ID |
highalarmgnsid |
This attribute is used for filtering on the GNS ID of a high alarm. |
Alphanumeric |
|
High Alarm Value |
highalarmvalue |
This attribute is used for filtering on the value of a high alarm. |
Alphanumeric |
|
High Deviation Enabled |
highdevenabled |
This attribute is used for filtering on whether a high deviation alarm bit is enabled. |
0 or 1 |
|
High Deviation GNS ID |
highdevgnsid |
This attribute is used for filtering on the GNS ID of a high deviation alarm. |
Alphanumeric |
|
High Deviation Value |
highdevvalue |
This attribute is used for filtering on the val ue of a high deviation alarm. |
Alphaumeric |
|
High OOR Enabled |
highoorenabled |
This attribute is used for filtering on whether a high out-of-range alarm bit is enabled. |
0 or 1 |
|
High OOR GNS ID |
highoorgnsid |
This attribute is used for filtering on the GNS ID of a high out-of-range alarm. |
Alphanumeric |
|
High OOR Value |
highoorvalue |
This attribute is used for filtering on the value of a high out-of-range alarm. |
Alphanumeric |
|
High Warning Enabled |
highwarningenabled |
This attribute is used for filtering on whether a high warning alarm bit is enabled. |
0 or 1 |
|
High Warning GNS ID |
highwarninggnsid |
This attribute is used for filtering on the GNS ID of a high warning alarm. |
Alphanumeric |
|
High Warning Value |
highwarningvalue |
This attribute is used for filtering on the value of a high warning alarm. |
Alphanumeric |
|
History Deadband |
historydeadband |
This attribute is used for filtering on the History Deadband of the alarm. |
Numeric |
|
Low Alarm Enabled |
lowalarmenabled |
This attribute is used for filtering on whether a low alarm bit is enabled. |
0 or 1 |
|
Low Alarm GNS ID |
lowalarmgnsid |
This attribute is used for filtering on the GNS ID of a low alarm. |
Alphanumeric |
|
Low Alarm Value |
lowalarmvalue |
This attribute is used for filtering on the value of a low alarm. |
Alphanumeric |
|
Low OOR Enabled |
lowoorenabled |
This attribute is used for filtering on whether a low out-of-range alarm bit is enabled. |
0 or 1 |
|
Low OOR GNS ID |
lowoorgnsid |
This attribute is used for filtering on the GNS ID of a low out-of-range alarm. |
Alphanumeric |
|
Low OOR Value |
lowoorvalue |
This attribute is used for filtering on the value of a low out-of-range alarm. |
Alphanumeric |
|
Low Warning Enabled |
lowwarningenabled |
This attribute is used for filtering on whether a low warning alarm bit is enabled. |
0 or 1 |
|
Low Warning GNS ID |
lowwarninggnsid |
This attribute is used for filtering on the GNS ID of a low warning alarm. |
Alphanumeric |
|
Low Warning Value |
lowwarningvalue |
This attribute is used for filtering on the value of a low warning alarm. |
Alphanumeric |
|
Maximum Setpoint |
maxsetpoint |
This attribute is used for filtering on the maximum setpoint for the alarm (PNT). |
Numeric |
|
Minimum Setpoint |
minsetpoint |
This attribute is used for filtering on the Minimum setpoint for the alarm (PNT). |
Numeric |
|
Report Alarm Delay |
reportalarmdelay |
This attribute is used for filtering on alarm reporting delay to the CAS or to the GNS. |
0 or 1 |
|
Report CAS |
reportcas |
This attribute is used for filtering on whether the alarm is reported to the CAS. |
0 or 1 |
|
Report GNS |
reportgns |
This attribute is used for filtering on whether the alarm is reported to the GNS. |
0 or 1 |
|
String Alarm 1 - 6 Enabled |
stringalarm1enabled stringalarm2enabled stringalarm3enabled stringalarm4enabled stringalarm5enabled stringalarm6enabled |
This attribute is used for filtering on whether a string alarm (1 - 6) is enabled. |
0 or 1 |
|
String Alarm 1 - 6 GNS ID |
stringalarm1gnsid stringalarm2gnsid stringalarm3gnsid stringalarm4gnsid stringalarm5gnsid stringalarm6gnsid |
This attribute is used for filtering on the GNS ID of a string alarm (1 - 6). |
Alphanumeric |
|
String Alarm 1 - 6 Value |
stringalarm1value stringalarm2value stringalarm3value stringalarm4value stringalarm5value stringalarm6value |
This attribute is used for filtering on the value of a string alarm (1 - 6). |
Alphanumeric |
Point: Scaling
See PNT Editor - Scaling Page for more information.
| Attribute | Attribute Name | Description | User Values |
|---|---|---|---|
|
Decimal Places |
decimalplaces |
This attribute is used for filtering on the number of decimal places that exist in Scaling portion of the alarm record. (Sixteen characters, including decimal digits, are allowed.) |
Numeric |
|
Decimal Places Flag |
decimal |
This attribute is used for filtering on an alarm that determines whether decimals are displayed. |
0 or 1 |
|
High Engineering Value |
enghigh |
This attribute is used for scaling and filtering on the High Engineering value for the alarm. |
Numeric |
|
Low Engineering Value |
englow |
This attribute is used for scaling and filtering on the Low Engineering value for the alarm. |
Numeric |
|
Raw High |
rawhigh |
This attribute is used for filtering on the alarm’s raw high value used in linear scaling. |
Numeric |
|
Raw Low |
rawlow |
This attribute is used for filtering on the alarm’s raw low value used in linear scaling. |
Numeric |
|
Scale Coefficient a0-a5 |
scalecoef_a0 scalecoef_a1 scalecoef_a2 scalecoef_a3 scalecoef_a4 scalecoef_a5 |
This attribute is used for filtering on the scale coefficient number for the alarm when polynomial curve fit coefficients are used. |
Numeric |
|
Scale Value |
scalevalue |
This attribute is used for filtering on the scaling value of the alarm. |
Numeric |
|
Use Two Point Scaling |
twopntscale |
This attribute is used for filtering on the two-point scaling in use for the alarm. |
Numeric |
Point: HyperPoint
See PNT Editor - HyperPoint Page for more information.
| Attribute | Attribute Name | Description | User Values |
|---|---|---|---|
|
Hyper Point Library Long ID |
hyperpointliblongid |
This attribute is used for filtering on the Hyper Point Library Long ID for the alarm. |
Alphanumeric |
|
Hyper Point Script Format Description |
hyperpointscriptfmt_desc |
This attribute is used for filtering on the Hyper Point Script format description for the alarm. |
Text |
|
Hyper Point Script Format |
hyperpointscriptfmt |
This attribute is used for filtering on the Hyper Point Script format for the alarm. |
Text |
|
Hyper Point Type |
hyperpointtype |
This attribute is used for filtering on the Hyper Point type for the alarm; for instance, "S" for "script." |
Text |
|
Hyper Point Type Description |
hyperpointtype_desc |
This attribute is used for filtering on the Hyper Point type description for the alarm. |
Text |
|
HyperPoint Enabled |
hyperpointenabled |
This attribute is used for filtering on whether Hyper Point is enabled for the alarm. |
0 or 1 |
|
Script Enabled |
scriptenabled |
This attribute is used for filtering on whether a script is enabled for the alarm. |
0 or 1 |
|
Script Version |
scriptversion |
This attribute is used for filtering on the script version for the alarm. |
Numeric |